What is the recommended evacuation procedure to remove moisture from a system?

Prepare for the ESCO Refrigeration Test. Practice with interactive quizzes featuring multiple choice questions, each with detailed explanations and hints. Boost your chances of success!

Multiple Choice

What is the recommended evacuation procedure to remove moisture from a system?

Explanation:
Moisture in a refrigeration system is removed by creating a deep vacuum so water vapor boils off at a lower pressure and can be drawn out of the oil and passages. The recommended procedure is to triple evacuate to about 500 microns using a deep vacuum pump. Doing multiple evacuations helps because each pull expels moisture that may outgas from oils and surfaces, then the subsequent deeper vacuum reaches residual moisture that the earlier pulls couldn’t remove. A single evacuation to around 1000 microns isn’t deep enough to guarantee dryness, while stopping at 2000 microns is far too shallow. Using a standard air compressor cannot create the necessary vacuum and would introduce air and moisture into the system.

Moisture in a refrigeration system is removed by creating a deep vacuum so water vapor boils off at a lower pressure and can be drawn out of the oil and passages. The recommended procedure is to triple evacuate to about 500 microns using a deep vacuum pump. Doing multiple evacuations helps because each pull expels moisture that may outgas from oils and surfaces, then the subsequent deeper vacuum reaches residual moisture that the earlier pulls couldn’t remove. A single evacuation to around 1000 microns isn’t deep enough to guarantee dryness, while stopping at 2000 microns is far too shallow. Using a standard air compressor cannot create the necessary vacuum and would introduce air and moisture into the system.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy